Re: ademco vista 20P expansion zone interior delay problem



autonut843 wrote:
>
> ...I notice when I program a zone on the 4229 as
> either type 04 interior follower or type 10 interior
> with delay, that, when armed in away mode, it
> causes an alarm event as if it were an instant
> perimeter type zone.

This is normal.  In the "away" mode all zones are active.  Follower zones
will heed the delay timer *if* you trip a delay zone *before* tripping the
follower zone.  If you trip a follower zone first, it behaves like an
instant perimeter zone.  The following is quoted from the installation
manual:

Type 04 Interior Follower
. Assign to a zone covering an area such as a foyer, lobby, or hallway
through which one must pass upon entry (to and from the keypad).
. Provides a delayed alarm (using the programmed entry 1 time) if the
entry/exit zone is faulted first. Otherwise this zone type gives an instant
alarm.
. Active when the panel is armed in the Away mode.
. Bypassed automatically when the panel is armed in the Stay or Instant
modes; if armed in Night-Stay mode, zones assigned to zone list 05
(night-stay zone list) are not bypassed when system armed in Night-Stay
mode.

> When I arm in stay mode it works as expected
> (no alarm event).

Also normal.  Follower and interior zones are bypassed in "stay" mode.
Note, however, that the zone behaves differently in "night stay" mode if it
is in List 5.

> When I arm in away mode I can enter through my
> entry delay 1 or entry delay 2 door, trip an interior
> follower zone wired into one of the first 8 zones
> wired into the main alarm board with no problems,
> but if I then trip the interior follower zone wired
> into the 4229 expansion zone, an alarm event occurs.

Hmm.  Things to check...  Have you by any chance miswired the zone?  I
assume you're using EOL resistors on the expansion zones.  Have you mapped
an expansion relay output to the zone for a siren trigger or is this alarm
event coming from the Vista-20 itself?


> Has anybody else ever had problems where a zone
> seems to work properly but does not when the alarm
> is armed in a certain way?

Was the system armed in "night stay" mode?  If so, the follower zones would
be active.

--

Regards,
Robert L Bass

=============================>
Bass Home Electronics
2291 Pine View Circle
Sarasota · Florida · 34231
877-722-8900 Sales & Tech Support
http://www.bassburglaralarms.com
=============================>




comp.home.automation Main Index | comp.home.automation Thread Index | comp.home.automation Home | Archives Home