[Message Prev][Message
Next][Thread Prev][Thread Next][Message
Index][Thread Index]
MCB ratings for CBus modules
Isn't the breaker in circuit to protect the cable not the fitting?
If the cable is 1.00 sq mm then it will carry 10 amps, so a 10amp or 6amp
MCB would be appropriate.
Why would you want to go as low as 1or 2 amps?
Tracey
>>
>> As far as i am aware "C" curve type circuit breakers are
normally used in
>> a
>> Domestic install here in Oz.....Wasnt aware of "B"
curve circuit
>> breakers(although have used "D"curve for motors) ,
which seems to be
>> what
>> people should be using on the load side for each dimmer
channel......
>> Would
>> be good to get something smaller than 6amp..........2amp available
in B
>> curve ???...........
> Under fault conditions (like a lamp blowing), the current seems to go
much
> higher than 6A
> anyway (since it trips a B type 10A & 16A MCB, although not a B
type 32A
> MCB) - so is
> there any practical difference between a 1A/2A MCB and a 6A one? Would
a
> 2A MCB of the
> same type as a 6A MCB trip first? I guess that since the current
reaches
> the limit of the
> 2A MCB fractionally before it reaches the limit of the 6A MCB, it is
> possible. But I
> would have (naively) thought that the difference in time is
insignificant.
>
> I can see there's a difference if you were worried about somebody
> installing lights that
> run beyond the 1A limit - but since this is a domestic install that I
> control, that's not
> going to happen.
>
--
No virus found in this outgoing message.
Checked by AVG Anti-Virus.
Version: 7.0.308 / Virus Database: 266.9.5 - Release Date: 07/04/2005