Re: Napco MA3000 - Dialer Test on both Lines?
This was a requirement that first appeared in the 1996 NFPA 72 edition to be
effective June 1998
NFPA 72-1996 Section 4-5.3.2.1.6.2
NFPA 72-1999 Section 5-5.3.2.1.6.2
state that both channels shall be tested at intervals not exceeding 24 hours
with an exception that if two lines (numbers) are used it shall be permitted
to test each line (number) at alternating 24-hour intervals
Unless the requirement has been removed in later editions, I believe you
will find that it is required for the 24 hour test to alternate between the
two lines or test both lines every 24 hours.
Doug
--
"Frank Olson" <Use_the_email_links@xxxxxxxxxxxxxxxxxxxxxx> wrote in message
news:Ejrvg.207985$iF6.2094@xxxxxxxxxxx
> Doug L wrote:
>> I think the NFPA 72 requirement is that the system alternates its daily
>> test between the two lines.
>>
>> Doug
>>
>
>
> My copy of NFPA 71 doesn't mention that. It only states that "each DACT
> shall automatically initiate and complete a test signal transmission
> sequence to its associated DACR at least once every 24 hours." AFAIK that
> remains the only requirement other than the one that states that failure
> of a telephone line shall be annunciated locally and transmitted to the
> DACR within 4 minutes on the second (backup) line.