[Message Prev][Message Next][Thread Prev][Thread Next][Message Index][Thread Index]

Re: Connecting two DMP alarms together? Outputs to Zones? Possible?



The best way to do this is remove the XR6 and put a fire rated zone expander
there in it's stead, using the 4 conductors from the house to the garage.
That will give 3 burg zones and one for the smokes. Then program the garage
keypad and zone expander as partition 2...bada bing..done and supervised.


"Jim" <alarminex@xxxxxxx> wrote in message
news:1136696675.202919.212620@xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx
|
| jsm174@xxxxxxxxx wrote:
| > Hello.
| >
| > I have two DMP alarm panels. I have an XR200 and a XRSuper6 - both in
| > different buildings approximately 100' away.
| >
| > I have the XRSuper6 configured to activate output 3 whenever a Fire
| > condition is triggered. It is also configured to activate output 4
| > whenever a Burglary condition is triggered.
| >
| > I am trying to tie those outputs into the XR200 as zones 7 and 8.
| >
| > I'm confused about how outputs work. From the manual:
| >
| > "The four annunicator outputs can be programmed to indicate the
| > activity ofthe panel's zones or conditions occurring on the system.
| > Annunciator outputs do not provide a voltage but instead
| > switch-to-ground voltage from another source."
| >
| > For my system to work correctly, it is almost like I need the outputs
| > to act like door contacts... Closed when not in alarm, and open when in
| > alarm.
| >
| > I've checked for continuity between the panel ground and the alarm
| > output, but it is always open. Thus when I try to arm the XR200, I'm
| > getting faults on zones 7 and 8.
| >
| > Has anyone ever tried to do something like this?
| >
| > Thanks,
| > -- Jason Millard
|
|
| You can do this, but I'd suggest that you make darn sure that it's
| acceptable by your AHJ. Fer sure ....It's not acceptable to do this in
| my area and you're sure taking a chance of something going seriously
| wrong ...... especially where the fire detection is concerned.
|
| Keep in mind that I'm not familiar with either of the panels you're
| using but this is how I'd guess you should be able to do it.
|
| Program the XR200 to require end of line resistors on zones 7 and 8.
| Install the resistors across the zone terminals. Program (lets say)
| zone 8 for fire and zone 7 for burglary. Run three wires from the XRS 6
| panel to the XR200.
|
| Connect one wire from a negative circuit (ground) terminal in the XRS6
| panel to a negative circuit (ground) terminal in the XR200  ( A
| "common" ground connection must exist between the panels ....... I
| don't mean "earth ground")
|
| Connect the second wire from "output 4" of the XRS6 to the positive
| terminal of zone 7 of the XR200, along with one end of the existing end
| of line resistor. ( when output 4 of the XRS6 goes negative, it will
| trip the zone.)
|
| Connect the third wire from "output 3" of the XRS6 to the coil of a
| sensitive relay  ( low current draw ie a few mills ... see Altronix)
| installed in the XR200        The other side of the relay coil should
| be connected to the aux positive output of the panel through a diode.
| The normally open contacts of the relay are connected across the end of
| line resistor on zone 7. ( when output 3 goes negative, the relay
| contacts will short out the resistor simulating a fire alarm.)
|
| I'm not sure of the negative "swing" of these panels or the current
| available, so it's possible that this wont work over the distance of
| wire that you're using. If you can, just to be on the safe side, you
| should run a couple of "4 wires" and double up on the wires for each of
| the three wire runs or run 18 guage wire. If it still doesn't work
| because of lack of current or "swing" to negative, you might try
| biasing outputs 3 and 4  of the SRX6, positive, through a 2.2K
| resistor.
|
| But ........ see what happens first.
|
| Keep in mind this is not a good thing to do. There's no supervision or,
| as a matter of fact, nothing about this, that sounds like it should be
| done.
|
|