On Jun 14, 11:03 am, "Robert L Bass" <RobertLB...@xxxxxxxxxxx> wrote:
> The zones on the 4208U expansion board should
> each be supervised using the 10K Ohm resistors
> that came with the 4208U.
>
> Have you set the address dip switches on the
> 4208U correctly?  Also, I assume you used twisted
> pair wiring for the polling loop.  You don't need it for
> analog sensors but it's required for the PL.
>
> Here's an excerpt from the Vista-50P concerning the
> polling loop:
>
> The built-in polling loop has the following limitations that must be obse=
rved:
>
> -- The maximum allowable current draw from the polling loop is 64mA. (Ref=
er to the POLLING LOOP CURRENT DRAW WORKSHEET (found in
> Section 15: FINAL POWER-UP PROCEDURE for current draws of various polling=
 loop devices.) If devices total more than 64 mA, a 4197
> Polling Loop Extender Module is required.
>
> -- Regardless of current draw, no more than 64 devices can be connected t=
o this loop. Installations which require up to 86 zones
> will require the use of zone expanders which accommodate more than one zo=
ne per RPM device (4190WH (2 zones) or 4208 (8 zones)). If
> more devices are needed, a 4197 Polling Loop Extender Module must be used.
>
> The 4197 Polling Loop Extender Module may be used to provide additional p=
olling loop current, to extend the polling loop wire run,
> and/or to provide individual, electrically isolated polling loops...
>
> --
>
> Regards,
> Robert L Bass
>
> =3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=
=3D=3D=3D=3D=3D>
> Bass Home Electronics
> 941-925-8650
> 4883 Fallcrest Circle
> Sarasota =B7 Florida =B7 34233http://www.bassburglaralarms.com
> =3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=
=3D=3D=3D=3D=3D>
>
>
>
> > Hi, Two Ademco problems:
>
> > I connected a 4208U to a Vista 50ADT Panel.  What should the zone type
> > be for the 4208 (zones 10-16).  I tried "07" - referenced by DIP
> > switch, and all the zones (which have the 10K resistors) come up as
> > fault zones, with an addition zone 97 as a fault zone (based upon the
> > 4208 faulting).  I do not have a resistor on the "A" zone which is not
> > used when you use zones 9-16.  Resistance (before power applied comes
> > up at approx. 9.8 K on my DVM (so I have the right resistors in).
> > Each zone is homerun to a single window that has foil.  Is their an
> > EOL that connects accross the polling loop, as the manual shows a
> > picture of something coming out of the right side of the first 4208U
> > (or is that just a symbol to mean protection zones)?  I also set the
> > zones up with the same protection zone as the first 9, and as a
> > perimeter zone (03).  On the 50P panel, I used 24 as + and 25 as -,
> > however, why is there a "+" sign under pin 25?
>
> >Continuing, I have the 50P manual.  There appears to be no manual (just =
dealer data sheets) for the 4208U.  All zones 10-16 on the 4208U show fault=
s=2E  For zones 10-16 I have the switches set for ON ON ON ON OFF OFF OFF O=
N, and zone type (50P) set for #7 (programmed zone by DIP Switch).  I even =
connected the EOL directly to loop B and it still gives me the fault readin=
g=2E  Can the panel lose it's programming for those zones, or did the origi=
nal owner never have the expansion zones turned on? as I had to enable them=
.  I'm currently testing the alarm with only 1 7amp battery, and 3 keypads =
(using a sonic alert as a temp siren (instead of the MVA1000 and 4 speakers=
)) so I don't think I have a current problem.  I also put a jumper across t=
he tamper switch, as it appears that the magnet (if there is one) in the 42=
08 cover is missing (although switch 8 should bypass it).  Since loop A is =
not used, I didn't put an EOL on it.  Is there an additional memory locatio=
n in the 50P to tell the system that a 4208 is installed?