[Message Prev][Message Next][Thread Prev][Thread Next][Message Index][Thread Index]

Re: 2006 IBC 2nd attempt



>> > "ABLE1" <royboynospam@xxxxxxxxxxxxx> wrote in message
>> > news:T9hql.5946$Za7.1965@xxxxxxxxxxxxxxxxxxxxxxxxxxxxxx
>> >> There is a whole lot more to the issue here than I have stated and
>> >> that
> I
>> >> will not
>> >> elaborate on for various reasons.  However, since I have started this
>> >> thread
>> >> I have found the answer.  (a friend loaned me his 2006 IBC)
>> >>
>> >> For those that don't know (which seems to be many) the answer is as
>> >> follows
>> >>
>> >>
>> >> [F] 907.2.7 Group M.  A manual fire alarm system shall be
>> >> installed in Group M occupancies having an occupant load
>> >> of 500 or more persons or more than 100 persons above
>> >> or below the lowest level of exit discharge.  The initiation of a
>> >> signal from a manual fire alarm box shall initiate alarm notification
>> >> appliances as required by Section 907.9.
>> >>
>> >> So that means that smokes are NOT required.
>> >
>> > got to have at least one protecting the panel. :)
>>
>>
>> Do you care to share the reference on that???
>>
>>


"RockyTSquirrel" <gafa@/nospam/usa.com> wrote in message
news:2aCdnVjh06ANezTUnZ2dnUVZ_hWWnZ2d@xxxxxxxxxxxxxxx
> NFPA 72
>
>



Its covered by 1.5.6 in the 1999 edition and by 4.4.5 in the 2007 edition,
there was and still is an option to use a heat detector if the environment
was unsuitable for a smoke detector. The 2007 edition added that a detector
was also required for notification appliance power extenders etc, but for
some strange reason in the 2007 edition an exception was introduced to allow
the omission of the detector for fully sprinklered buildings. I don't know
where you are located but you should check with your local AHJ because some
jurisdictions deleted that exception when adopting the code.