RE: Comfort Alarm / PIR Wiring
Brian
I've used these and didn't need a relay. The Comfort II installation
manual
covers this on Page 36:
Negative Applied Detectors
Certain types of detector such as outside PIR's and photocells provide an
open-collector output as a trigger rather than a relay output. This type of
signal can be connected directly into a zone terminal providing it is a
negative signal in one state and 'floating' in the other state. If the
signal
goes negative when detecting, use a normally-open zone type such as
Type '8' (normally-open switch). This is suitable for light sensors or
external non-alarming detectors which may be used as monitors to drive
Responses for lighting and CCTV applications.
The negative signal should be applied to non-eol zone where the trigger
wire connects just to one side of the zone, provided the detector has a
12v supply derived from the panel acting as a reference.
If tamper protection is required on the zone, three wires will be required
and the zone jumper should be removed from the header. A single 2K7
resistor should be fitted in series with two of the wires at the detector.
The detector's negative trigger should then connect to the side of the
resistor and wire which returns to the zone terminal and NOT to the wire
that returns to the zone COM terminal, which is already at 0V .
'GJD XL or Opal' detectors have both -ve alarm trigger outputs and a
built-in photocell -ve output. Comfort 'default ' uses zone 13 for a light
sensor.
It's been a while since I installed but I think you need 3 wires for basic
operation 12v, 0v and -ve trigger (which you connect to the zone)
Sure I had a document relating to this. I'll see if I can find it.
HTH
Pete
From: ukha_d@xxxxxxx [mailto:ukha_d@xxxxxxx] On Behalf Of
Brian Smith
Sent: 12 October 2013 17:26
To: ukha_d@xxxxxxx
Subject: [ukha_d] Comfort Alarm / PIR Wiring
Afternoon all
I am just trying to install my Comfort alarm and need some help with the
wiring on some external PIRs I have. I was hoping to wire them as standard
zone inputs like internal PIRs but now I'm reading the instructions it
might
not be that simple.
The instructions seem to suggest I might need a relay in order to create
what I assume is a normal volt free loop that Comfort can use but I
wandered
if any of you clever people out there could tell me otherwise.
The instructions for the PIR are here:-
http://www.gjd.co.uk/wp-content/uploads/wpsc/downloadables/Opal-XL-Technical
-Manual-UK.pdf
Any suggestions as to how I can wire in to Comfort with the minimum of fuss
would be much appreciated.
Thanks
Brian